Hello Solar Friends:
I wrote last Spring about an issue we were having with our grid-tied inverter (Trace/Xantrex 4024 w/battery backup), which would disconnect from the grid for a few hours mid-day on weekdays but not on weekends, nor when it was cloudy. Two solar installers reviewed our installation and concluded the problem was not with our system, and to contact our local utility, Pacific Gas & Electric.
Last Summer I had them out and carefully scheduled it so the technician would arrive mid-day; he quickly noted our incoming grid voltage was 256, which was out of spec for the nominal 240 (they're allowed to be within 5% of 240; between 228 to 252). He made a call and identified a boosting device on our block that boosted the voltage on weekdays but not on weekends (one mystery solved), and turned the thing off.
However, peak voltage on a sunny days was still hitting 253, and the inverter still dropping, so I had a second PG&E technician out; he arrived in the evening, when voltage had fallen to within spec, so he could do nothing. Side note: there are many PV systems on our block, which is causing the mid-day voltage to climb. Called again and a third technician lowered it further, to a peak of 248. The inverter is now staying connected, and the charge controller recording 2 to 3 times the daily kWh we were collecting in July when it was dropping consistently.
Mystery solved, and worth sharing in case anyone is having similar issues ... check your grid voltage!
David Arkin - Albany, California
* * * * *
Arkin Tilt Architects
Ecological Planning & Design
with a fundraising goal of $2,500 to support CASBA. Thank you!
David Arkin, AIA, ArchitectLEED Accredited ProfessionalCA #C22459/NV #5030/OR #6738
1101 8th St. #180, Berkeley, CA 94710510/528-9830 ext. 202www.arkintilt.com"There is no way to peace. Peace is the way."- A. J. Muste