    This week we take a look at grid defection - are technology, utility policies, and economics at the point where it just does not make sense to stay connected to the grid? Each Tuesday at noon (Eastern) solarPVtraining.com hosts a Zoom sessions for students (or anyone, really) interested in solar. Generally discussion focuses on technical questions, problems or troubleshooting - or just what is happening in solar that week.



    ------------------------------
    Jay Warmke
    Owner
    Solar PV Training LLC
    ------------------------------


  • 2.  RE: Solar Noon Tuesday - Grid Defection, is it time to disconnect from the electrical grid?

    Silver
    Contributor
    Posted 21 days ago

    Listen to it after the fact. Over all pretty good. I have one bone to pick. Near the end when you were talking about over sold transformers in your 10 houses on one 50KW transformer, you added to the load on the transformer for the producers when producing. That is wrong. If you have multiple houses (meters) on one transformer, they are connected in parallel to the SECONDARY!! Not the primary. In short the over production services directly to the load of the non producers which actually reduces the load on the transformer, not increasing it. I have this situation on my installed 50KW trans that I had put in when I ran my power feed underground. I have 3 houses on my trans (Including me). When I am producing, my overproduction goes directly to my neighbors meters, never making it to the primary side. Thus reducing the load on the trans. The only way production from multiple houses becomes load is when all production exceeds all load combined, then it crosses over from the secondary to the primary, as production load. In short they are NEVER additive....



    ------------------------------
    william fitch
    Owner
    www.WeAreSolar.com
    ------------------------------



  • 3.  RE: Solar Noon Tuesday - Grid Defection, is it time to disconnect from the electrical grid?

    Posted 20 days ago

    William,

    Your depth of knowledge is appreciated and enlightening.  I'm also a regular attendee of Jay's "Solar Noon" series and have heard the banter regarding utility transformers.  In Jay's defense, his stated point last Tuesday, regardeing the capacity of utility transformers for accepting back feed from customer PV systems, is the excuse we hear from the utility companies.  They claim their transformers do not have the capacity to redistribute line power from multiple PV systems.  This is their rationale, true or not, to limit (total KV) PV systems.

    I think we have two knowledge paths forward.  First, can you elaborate, with more detail, on your statement regarding PV system backfeed remaining on the secondary side (transformer output) of utility power distribution?  And second, looking at the broader utility perspective, should grid system engineering begin to focus on transformers / new devices that can better manage PV backfeed onto both secondary and primary sides of the grid?

    I look forward to your response.



    ------------------------------
    [Dennis] [Garde AIA, LEED AP]
    [Construction Manager, Lisbon]
    [US Dept. of State / OBO]
    [Savannah] [GA]
    [Dennis.Garde@gmail.com]
    ------------------------------



  • 4.  RE: Solar Noon Tuesday - Grid Defection, is it time to disconnect from the electrical grid?

    Silver
    Contributor
    Posted 20 days ago
    Edited by william fitch 20 days ago

    Hi: Yes, after the fact the thought you expressed about the utility "excuse" crossed my mind. But I was trying to just talk about the engineering of the situation, not any added BS. 

    Being more granular.... I mean its pretty basic Physics. Electricity will always flow from the higher voltage to the lower. In a simple transformer, you have two voltages; The primary and the secondary. If the direction of power is from the low voltage side to the high voltage side, it is called then a step up transformer. If the power flow is from the high voltage side to the low voltage side (Typical pole transformer) it is called a step down transformer. Now I know above I said electricity always flows from high to low, and what I just described about transformers may seem to contradict that, but it does not..

    A transformer has a ratio of windings. You have "so many turns" on the primary side, and you have "so many turns" on the secondary side. This ratio determines the relationship between the two voltages on the transformer. So as an example, if you have a transformer that has 100 turns on the primary side, and 10 turns on the secondary side, the ration is 10 to 1. So, if you feed 100VAC to the primary side, 10VAC will result on the secondary side. Or if you have a ratio of 32 to 1, you can feed 7700VAC to the primary side and get 240VAC on the secondary side.  In that scenario it is functioning as a step down. Now, back to the appeared "contradiction." If you start increasing the voltage on the secondary side (240VAC) by added energy production, the voltage will rise and push back the other direction. Meaning technically, you are increasing the voltage of the primary side (7700vac). So the "always from high to low" in this case means you are raising the baseline secondary voltage from 240vac to maybe 241vac. The electricity will reverse flow from the high (Added energy) to the original base line (240vac.) and go out the primary. 

    I hope this does not sound to confusing. This would be much easier in a class room where I could "speak" and draw all this. Text only is limiting. 

    So anyway, the additional houses are added on the secondary side ONLY, in parallel. Think plus to plus and minus to minus.  So if one house is producing energy (Higher voltage) than the others, as the high to low rules goes, the power will just flow from the one house to the other, leaving the transformer OUT OF THE LOOP. Its secondary terminals just become a connection point, sort of. Now the power effect is that whatever the load of the lower voltage house is, lets say 2000 watts, that power is now satisfied by the higher house, there by actually reducing the power coming through the transformer by 2000 watts, assuming the extra production of the higher house is in fact 2000 watts. So as I said in my original post, the load on the transformer is actually reduced. As more and more power is added from the secondary side, you will eventually reach a point where the power through the transformer is zero. Total demand destruction (From the transformers perspective). If the power keeps increasing on the secondary side, the flow becomes "backwards" and power is given to the utility by actually increasing the voltage on the primary side, 7700 vac in this example (Step up transformer).

    As far as shifting off transformers for some other way to control, transformers are wonderful devices. They are simple, tough, reliable and efficient, highly EMR resistant compared to IC solutions. 

    I tried to find all my typos in there, and I  hope I got them all.

    Hope that helps....

    .....Bill



    ------------------------------
    william fitch
    Owner
    www.WeAreSolar.com
    ------------------------------



  • 5.  RE: Solar Noon Tuesday - Grid Defection, is it time to disconnect from the electrical grid?

    Posted 19 days ago

    Thanks William,

    You're right, it is difficult to explain transformer details / principles without classroom & teacher tools.  However, you succeeded.  The images below are of a single phase META, pole transformer manufactured in Florida, and the specs.  Following your description, the primary side / utlity feed are the high voltage bushings and the secondary side are the low voltage bushings.  The number of customers (potentially) served from the secondary side depends on the size of the transformer.

    Steven Hegedus, Professor / Scientist has joined the conversation and confirms the engineering obvious, that the transformer and the grid do not care much about the direction of electron flow.  The utility's objection to backfeeding the grid from PV systems is contractual.  But taking their objection to the logical end, at least to the sub-station, there are huncreds of customers and dozens of transformers downstream from the sub-station.  The likelyhood of backfeeding through the sub-station to the regional power providers seems like an engineering hurdle that can overcome the contractual objections.  But try convincing PJM of that.

    Cheers...



    ------------------------------
    [Dennis] [Garde AIA, LEED AP]
    [Construction Manager, Lisbon]
    [US Dept. of State / OBO]
    [Savannah] [GA]
    [Dennis.Garde@gmail.com]
    ------------------------------



  • 6.  RE: Solar Noon Tuesday - Grid Defection, is it time to disconnect from the electrical grid?

    Silver
    Contributor
    Posted 19 days ago

    Hi: Yes, you are right. If you want to see the real nature of their objections, look no further to them winning about solar and RE contributors when the gird % of contribution was in the single digits, even during peak sunshine hours. Its the same deal with EV's tearing up the roads, so tax them, when they are less than 10% of the "traffic". It ALL comes down to lost profit, every-time (For the FFI), no matter what the exact system dynamics are....



    ------------------------------
    william fitch
    Owner
    www.WeAreSolar.com
    ------------------------------



  • 7.  RE: Solar Noon Tuesday - Grid Defection, is it time to disconnect from the electrical grid?

    ASES Life Member
    Posted 19 days ago

    William - What you say is correct IF the other homes sharing the transformer's secondary are using your excess generation.  But often the excess occurs midday when the sun is shining and people are at work, with their homes possibly not using much power.  I think you would have to meter the other homes while you're exporting in order to verify what you're claiming.  Absent that data, it's just speculation.



    ------------------------------
    Mike Curran
    Retired EE
    ------------------------------



  • 8.  RE: Solar Noon Tuesday - Grid Defection, is it time to disconnect from the electrical grid?

    Silver
    Contributor
    Posted 18 days ago
    Edited by Ella Nielsen 8 days ago

    I'm sorry, what exactly are you saying I am claiming, specifically???

    To be blunt, your response makes no sense regarding the description I laid out regarding parallel houses, or how transformers work...

    ------------------------------
    william fitch
    Owner
    www.WeAreSolar.com
    ------------------------------



  • 9.  RE: Solar Noon Tuesday - Grid Defection, is it time to disconnect from the electrical grid?

    ASES Life Member
    Posted 18 days ago

    Maybe I missed something in your other replies...

    To make an extreme example, let's say the other houses sharing the transformer's secondary with yours are all unoccupied and using no power.  Then all your excess generation passes through to the primary.  Though this is unlikely, it illustrates my point.  Whether or not your excess makes it to the primary all depends on how much of that excess gets used by your neighbors.  The less they use, the more likely the transformer primary will see the power passed through to it.  I don't think you can assume that all your excess generation is getting used by your neighbors sharing your transformer's secondary.



    ------------------------------
    Mike Curran
    Retired EE
    ------------------------------



  • 10.  RE: Solar Noon Tuesday - Grid Defection, is it time to disconnect from the electrical grid?

    Silver
    Contributor
    Posted 18 days ago

    Your right. You didn't read it all. I covered that.



    ------------------------------
    william fitch
    Owner
    www.WeAreSolar.com
    ------------------------------



  • 11.  RE: Solar Noon Tuesday - Grid Defection, is it time to disconnect from the electrical grid?

    ASES Life Member
    Posted 19 days ago
    This is in response to discussion between Will Fitch and Denis Garde. Concern about PV back feeding into utility transformers is a very common reason for utilities to ban residential or community solar on selected distribution circuits. I have asked several times about justifying this. One reason I have heard repeatedly is if the substation is fed by the transmission network, Then back feeding from the transformer means injecting power into the transmission system. Most distribution utilities have contracts with the regional grid operator (like PJM in the mid Atlantic or MISO in Midwest) which forbid them to do this. This is a contactual not physics-based objection. 

    I would like to know what are the physical objections in terms of back flow through other components - breakers, reclosers, and transformers themselves? 

    Steve 

    Steven Hegedus
    Professor, Electrical and Computer Engineering (retired) 
    Senior Scientist, Institute of Energy Conversion (retired) 
    University of Delaware
    Newark DE 19716
    302-831-6253 message only
    ssh@udel.edu

    Co-editor, Handbook of Photovoltaic Science and Engineering, 2nd Ed 
    (Wiley and Sons 2011) 












  • 12.  RE: Solar Noon Tuesday - Grid Defection, is it time to disconnect from the electrical grid?

    Silver
    Contributor
    Posted 19 days ago

    Hi: To my understandings, a transformer does not care which way the power flows. It performs the same way up or down. Changing the flow direction does not change any of the relationships between voltage and its location in relation to the core, which would be a REAL problem, if it did. But it does not. Any power generation that is NOT THEIRS is lost revenue. Think of this example. Suppose you had a single phase line running down a street with 40 houses. Over time (Years) 10 more houses get added. That is more energy needed ($$$$) and more load on that line. Having say 20 of those houses now starting to generate their own power and over producing as well, is like losing the business of those 10 extra houses, with the added negative of the peak demand possibly remaining the same (Nighttime loads). So less business but potentially more volatility. More volatility is really not an issue in and of itself. A commercial business like a foundry can add a crap load of volatility to a line across multiple phases. But they "swallow it" because they are making more money. With people genning their own, it becomes a bitter pill. Demand destruction. This is why you see tax's against solar producers, resistance to net metering, on and on. People genning their own does NOT FIT a Capitalist's model. The whole grid should be socialized, but that is another discussion.

    AS for REAL physical objections that are not rounding errors, I think one would be hard pressed to find any.



    ------------------------------
    william fitch
    Owner
    www.WeAreSolar.com
    ------------------------------